mike20793
Structural
- Jun 26, 2014
- 680
I recently designed a retaining wall that had a CMU screen wall above it for IBC 2012. I had #5's at 24 inches in the CMU and #5's at 12 inches centered in the stem of the retaining wall, so I extended alternating bars from the stem to lap splice the CMU vertical reinforcement. When I detailed it, then double checked it, I noticed that for a #5 bar, the tension lap splice length for CMU is less than the Class B tension lap splice length for the concrete. For CMU (f'm=2000 psi) the lap splice comes out to about 20 inches but for concrete (f'c=4000 psi) it comes out to 31 inches using the provisions of 12.2.2. This seems counter intuitive to me. I understand 12.2.3 can decrease the lap splice length in concrete based on confinement of transverse reinforcement, but TMS 402 also has a provision to reduce the lap splice length. Has anyone else noticed this before? Does anyone know why this is the case? I'm having a hard time convincing myself that coarse grout and medium weight CMU can develop and splice a bar in a shorter distance than concrete.