DavidCR
Mechanical
- Jan 10, 2002
- 355
I work for an electric power and telecomunications company.
For most of our facilities there are electric equipment pannels every where and I consider that following NFPA 10 most of our facilities involve A:C fires.
People here have a strong preference with CO2 extinguishers since they are very reluctant to withstand with the possibility of cleaning the mess related with dry chemical of A:B:C extinguishers on expensive electric equipment.
So for years we have used CO2 portable extinguishers, are listed for B:C fires only.
I have to make a proposal for an hydroelectric power plant, I want to follow NFPA 10 and I´m thinking that in general ABC dry chemical extinguishers are the recomended choice. Mostly A:C fires with some possibility of B fires.
People here want to use CO2 extinguishers anyway, but I have told them that the ABC dry chemical extinguishers is a more effective choice and its initial cost is cheaper, also that CO2 may damage equipment due to thermal shock.
We also have B:C fires (dealing with some areas where lubricatng oil is present)but our questions deals more with the general areas.
I want to more clear in some aspects, so my questions are:
a). Is it a good choice to provide ABC dry chemical and also CO2 extinguishers?. Is it a good practice, or it can be a confusion or a contradiction with the NFPA10.
b) Is there some points that can lead to a decision of using CO2 instead of ABC considering the risk of electric cabinets of a power plant.
c) Are water mist extinguishers a good choice as an alternative for our case?.
d) Am I correct asuming that an electric cabinet is an A:C risk considering the type of extinguisher to be used?
We also have other fire protection equipment, automatic sprinklers and nozzles, a good detection system, trained personnel, and others mentioned by NFPA 851 for hydroelectric power plants.
An external AHJ or insurance people have not helped much in this case, they just want to have the extinguishers following NFPA10 and they dont care much of the type of extinguisher used.
For most of our facilities there are electric equipment pannels every where and I consider that following NFPA 10 most of our facilities involve A:C fires.
People here have a strong preference with CO2 extinguishers since they are very reluctant to withstand with the possibility of cleaning the mess related with dry chemical of A:B:C extinguishers on expensive electric equipment.
So for years we have used CO2 portable extinguishers, are listed for B:C fires only.
I have to make a proposal for an hydroelectric power plant, I want to follow NFPA 10 and I´m thinking that in general ABC dry chemical extinguishers are the recomended choice. Mostly A:C fires with some possibility of B fires.
People here want to use CO2 extinguishers anyway, but I have told them that the ABC dry chemical extinguishers is a more effective choice and its initial cost is cheaper, also that CO2 may damage equipment due to thermal shock.
We also have B:C fires (dealing with some areas where lubricatng oil is present)but our questions deals more with the general areas.
I want to more clear in some aspects, so my questions are:
a). Is it a good choice to provide ABC dry chemical and also CO2 extinguishers?. Is it a good practice, or it can be a confusion or a contradiction with the NFPA10.
b) Is there some points that can lead to a decision of using CO2 instead of ABC considering the risk of electric cabinets of a power plant.
c) Are water mist extinguishers a good choice as an alternative for our case?.
d) Am I correct asuming that an electric cabinet is an A:C risk considering the type of extinguisher to be used?
We also have other fire protection equipment, automatic sprinklers and nozzles, a good detection system, trained personnel, and others mentioned by NFPA 851 for hydroelectric power plants.
An external AHJ or insurance people have not helped much in this case, they just want to have the extinguishers following NFPA10 and they dont care much of the type of extinguisher used.