We have a stoker fed, moving grate coal fired boiler, which has a backup gas fired auxiliary/emergency backup burner. In order for the gas burner to fire immediately on the start command, a scanner looking at the coal fire has to sense the presence of a coal flame. If no flame is detected, the gas burner will go through a 5 minute purge cycle before lighting off. This is the safety feature that assures the gas burner can not light if there is no boiler flame present. Obviously, a 5 minute purge is required when lighting the gas burner on a cold boiler. In an emergency, with the coal fired boiler operating, we do not want to wait 5 minutes before getting the gas burner in operation. We have tried a variety of scanner types, IR, near IR, UV, etc. I understand that a coal fire operates in the range of 3,500 to 5,500 Angstroms.
There are two components to the flame we are sensing; the DC component which is the energy level sensed from the brightness of the flame, and the AC component, which is the flicker frequency of the flame. Having a large burning surface ~ 20' x 20', this is a "lazy fire" compared to forced air combustion systems. The problem that I am experiencing is that I can tune the scanner for the AC and DC components of the flame for normal load conditions, but when the boiler goes to low load conditions, such as when production is down for the weekend, the scanner does not respond well to the reduction or difference in the AC and DC component. I have also found that there are several significant AC flicker frequencies at any given load, making it difficult to lock the scanner in on a predominant frequency. Does anyone have any success stories with an installation similar to ours?
There are two components to the flame we are sensing; the DC component which is the energy level sensed from the brightness of the flame, and the AC component, which is the flicker frequency of the flame. Having a large burning surface ~ 20' x 20', this is a "lazy fire" compared to forced air combustion systems. The problem that I am experiencing is that I can tune the scanner for the AC and DC components of the flame for normal load conditions, but when the boiler goes to low load conditions, such as when production is down for the weekend, the scanner does not respond well to the reduction or difference in the AC and DC component. I have also found that there are several significant AC flicker frequencies at any given load, making it difficult to lock the scanner in on a predominant frequency. Does anyone have any success stories with an installation similar to ours?