My situation falls under Chicago Code, but I would appreciate input from anyone who has run across this. I am sizing up combustion air for a large boiler plant - probably eight (8) 700BHP boilers. It will be an N+1 design. Two questions:
1. Do I need to size the combustion air for that "Plus 1" boiler even though it is not supposed to run unless another one fails?
2. The boilers will run on natural gas; however, they also have oil as a backup. I am delivering combustion air by mechanical means. The Chicago code requires 0.35 CFM per 1,000 BTUH for gas, and 0.4167 CFM per 1,000 BTUH for oil. Do I have to size the combustion air for oil (which is larger) even though the oil will only be used in an emergency if the gas supply fails?
Thank you for you help.
1. Do I need to size the combustion air for that "Plus 1" boiler even though it is not supposed to run unless another one fails?
2. The boilers will run on natural gas; however, they also have oil as a backup. I am delivering combustion air by mechanical means. The Chicago code requires 0.35 CFM per 1,000 BTUH for gas, and 0.4167 CFM per 1,000 BTUH for oil. Do I have to size the combustion air for oil (which is larger) even though the oil will only be used in an emergency if the gas supply fails?