offshorehvac
Mechanical
- Apr 15, 2008
- 32
Hi friends
Can someone please verify and clarify?
Application: Offshore Rig
Area of operation: North Sea
System X
Ambient : 72*F/80%RH
Inside required in Summer : 75*F/50%RH
Loads/Airflows
Room Sensible Load : 187000 BTU/Hr
SHR : 0.89
Supply air: 15000 CFM
Fresh air : 6100 CFM
Return Air: 8900 CFM
Air flows are based on minimum air changes requirements as per offshore regulations
Mix air conditions : (6100x72+8900x75)/15000=73.78*F/68%RH
(RH for mix air is from psy chart)
Supply air temp
187000=1.1 x 15000 (75-Ts)
Ts = 60.7*F/68%RH
When RSHR line is extended on saturation curve it gives an ADP of 47.5*F
For simplicity I have neglected Bypass Factor/Fan heat gain etc..
My Questions are:
1. What is the meaning of ADP 47.5*F and supply temp of 60.7*F. Do we have to cool down the air to 47.5*F and then raise the temp to 60.7*F.
2. Coil capacity should be calculated based on Enthalpy difference for Mix temp and ADP or Mix and Supply Temp.
Thanks
Can someone please verify and clarify?
Application: Offshore Rig
Area of operation: North Sea
System X
Ambient : 72*F/80%RH
Inside required in Summer : 75*F/50%RH
Loads/Airflows
Room Sensible Load : 187000 BTU/Hr
SHR : 0.89
Supply air: 15000 CFM
Fresh air : 6100 CFM
Return Air: 8900 CFM
Air flows are based on minimum air changes requirements as per offshore regulations
Mix air conditions : (6100x72+8900x75)/15000=73.78*F/68%RH
(RH for mix air is from psy chart)
Supply air temp
187000=1.1 x 15000 (75-Ts)
Ts = 60.7*F/68%RH
When RSHR line is extended on saturation curve it gives an ADP of 47.5*F
For simplicity I have neglected Bypass Factor/Fan heat gain etc..
My Questions are:
1. What is the meaning of ADP 47.5*F and supply temp of 60.7*F. Do we have to cool down the air to 47.5*F and then raise the temp to 60.7*F.
2. Coil capacity should be calculated based on Enthalpy difference for Mix temp and ADP or Mix and Supply Temp.
Thanks