I have an 8" thick slab with a 5'-0" span over a utility chase. The contractor was replacing some concrete and they saw-cut completely through the slab about 4" short of the side wall. Slab is drive way for truck traffic.
The proposed repair is to dowel in some #6 bars @6" OC and re-pour the edge.
I checked the dowel as an embed using Profis, and the capacity is about 3 kips and controlled by side break out.
I checked it using shear friction and the capacity is about 19 kips.
I read previous threads about full development length. If I use an epoxy and embed long enough to develop the rebar is that valid?
If I have to use development length, then I need to replace the slab.
My "feeling" is that the embed analogy is conservative and that the shear friction check seems like a lot of capacity. I don't have a lot of experience in this type of repair. In the past when this occurred, we used permanent post shores in the pit. I may do the same here.
I appreciate any advice you all may have.
The proposed repair is to dowel in some #6 bars @6" OC and re-pour the edge.
I checked the dowel as an embed using Profis, and the capacity is about 3 kips and controlled by side break out.
I checked it using shear friction and the capacity is about 19 kips.
I read previous threads about full development length. If I use an epoxy and embed long enough to develop the rebar is that valid?
If I have to use development length, then I need to replace the slab.
My "feeling" is that the embed analogy is conservative and that the shear friction check seems like a lot of capacity. I don't have a lot of experience in this type of repair. In the past when this occurred, we used permanent post shores in the pit. I may do the same here.
I appreciate any advice you all may have.