Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Cold weather concrete placement montoring

Status
Not open for further replies.

thatsmisterinspector

Geotechnical
Feb 27, 2011
1
It was recently come up on several job sites the question of where and how exactly you should monitor the temperature of concrete placed in cold weather. One job, they want us to place a hi/lo thermometer under the blankets and measure the surface temperature of the concrete for the first three (3) days. However, on other job they want us to place tubes in the concrete to check the internal temperature of the concrete. I have not been able to find where ACI, VDOT, or any other agencies indicate if the required temperature that concrete should be maintained; is internal or surface. Anyone had any suggestions?

 
Replies continue below

Recommended for you

ACI 306, section 4-4 is clear, monitor the concrete surface temperature. during cold weather, internal temperature will be higher than surface temperature and should be monitored also if excessive heating is anticipated
 
ACI has both cold weather and hot weather techniques. Check them out.
 