sjhgeotech
Geotechnical
- May 8, 2006
- 17
I have a steel column baseplate that is connected to a concrete foundation with anchor bolts. The anchor bolt nuts have corroded off and there is no way to get new nuts on the connection. The column is one leg of a four legged radio tower and is in complete tension of about 55 kips, max load. The best solution is to cap the existing baseplate with a concrete block that is connected to the existing foundtion using grouted rebar. I am assuming that I will use Section 12.2.2 of ACI-318 to determine the embedment length of the bars in the existing foundation. How many bars should be used if I am using #8 bars. A single 60 ksi bar would give me 60 kips of capacity but I think four bars would give me the symmetry I need. Is there a pull-out cone for each bar that I need to assume that subtracts from the full tension capacity?
Thanks.