Hi Group,
I had a column with a 10"x10"x1/2" base plate with 2-3/4" sitting on 1.5" grout for a project. The contractor somehow did not get the top of footing and anchor bolt location correct. The underside of the baseplate is 3.5" from top of pier. They ended up slotting existing holes to fit the anchor bolts (now have a bigger hole) and provided a thick washer plate welded to the top of base plate.
Typically, I consider the grout to provide lateral support to the anchor bolt and check the anchor rods in pure shear at the top of the grout (I take 0.8 times the shear strength of the anchor rod considering the reduction due to grout).
My problem is now is that the hole at the bottom will not bear against the anchor rod and load will transfer from washer plate to top of grout by bending the anchor bolt. I do not have sufficient bending capacity and have also checked to approach this by checking the interface shear (friction) and cannot get the required capacity.
I am looking for suggestions how to best connect the anchor rod to the underside of the base plate so that the rod does not undergo any bending and only go into shear. Note that the column is already up with the base plate and we have 3.5" of space to work with. Bolts in shear alone and concrete pier are OK for the applied loads. I was thinking of adding stiffener plates (shown in cyan in the sketch below) adjacent to the bolts at the bottom welded to the baseplate and anchor rod to prevent bending of the bolts.

Appreciate the help in advance!
I had a column with a 10"x10"x1/2" base plate with 2-3/4" sitting on 1.5" grout for a project. The contractor somehow did not get the top of footing and anchor bolt location correct. The underside of the baseplate is 3.5" from top of pier. They ended up slotting existing holes to fit the anchor bolts (now have a bigger hole) and provided a thick washer plate welded to the top of base plate.
Typically, I consider the grout to provide lateral support to the anchor bolt and check the anchor rods in pure shear at the top of the grout (I take 0.8 times the shear strength of the anchor rod considering the reduction due to grout).
My problem is now is that the hole at the bottom will not bear against the anchor rod and load will transfer from washer plate to top of grout by bending the anchor bolt. I do not have sufficient bending capacity and have also checked to approach this by checking the interface shear (friction) and cannot get the required capacity.
I am looking for suggestions how to best connect the anchor rod to the underside of the base plate so that the rod does not undergo any bending and only go into shear. Note that the column is already up with the base plate and we have 3.5" of space to work with. Bolts in shear alone and concrete pier are OK for the applied loads. I was thinking of adding stiffener plates (shown in cyan in the sketch below) adjacent to the bolts at the bottom welded to the baseplate and anchor rod to prevent bending of the bolts.

Appreciate the help in advance!