I am designing a 7.0 m two storey tall HSS column and I want to brace it with the bottom chord of the strut joist at mid height to reduce effective length. My question is how do you calculate for the axial load induced in the bottom chord of the strut joist?
 
Replies continue below

Recommended for you

The braces is generally designed for a capacity of 2% - 2.5% of the force resisted by the compression portion of the column.

"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
 
You also have to make sure it is stiff enough to act as a brace too. Appendix 6 is where you need to go. The brace force can also be reduced per the commentary of appendix 6 if the brace force is larger than that required.
 