KootK
Structural
- Oct 16, 2001
- 18,085
I'm peer reviewing some designs for column reinforcement where 8x8 columns have been whacked by forklifts about 18" above floor level. See the photo below. Our engineer has followed the lead of a previous firm and recommended angle reinforcement on the four corners of the column. My feeling is that no reinforcing is required. These three arguments inform my opinion:
1) The damage is far away from the mid-height of the column where full section stiffness is needed to prevent buckling.
2) There is no column "kink" to speak of. The column is still very straight. It just has the dents now.
3) While some of the cross section near the damage may be unable to carry compression due to P-Delta effects in the bent walls, I feel that I only need to demonstrate that there's enough undamaged section available to carry the load across the damage using squash capacity (As x Fy). I can get this done if I represent the four corners of the columns as imaginary 1.5" x 1.5" angles composed of undamaged HSS wall section. It doesn't take much. Moreover, there's probably some post buckling capacity to be had in the dented HSS side walls anyhow.
It might ultimately be prudent to fence off or concrete encase the columns to protect them from this kind of damage in the future. For now, however, I'd like to solicit comments regarding my "do nothing" proposal and the logic that I've used to justify it. The fact that reinforcement was specified by another firm in the past makes it apparent that one of us must be wrong in our thinking. Maybe it's me.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
1) The damage is far away from the mid-height of the column where full section stiffness is needed to prevent buckling.
2) There is no column "kink" to speak of. The column is still very straight. It just has the dents now.
3) While some of the cross section near the damage may be unable to carry compression due to P-Delta effects in the bent walls, I feel that I only need to demonstrate that there's enough undamaged section available to carry the load across the damage using squash capacity (As x Fy). I can get this done if I represent the four corners of the columns as imaginary 1.5" x 1.5" angles composed of undamaged HSS wall section. It doesn't take much. Moreover, there's probably some post buckling capacity to be had in the dented HSS side walls anyhow.
It might ultimately be prudent to fence off or concrete encase the columns to protect them from this kind of damage in the future. For now, however, I'd like to solicit comments regarding my "do nothing" proposal and the logic that I've used to justify it. The fact that reinforcement was specified by another firm in the past makes it apparent that one of us must be wrong in our thinking. Maybe it's me.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.