milkshakelake
Structural
- Jul 15, 2013
- 1,176
Which is the correct way to calculate axial loads on concrete columns: tributary area, or analysis using continuity of the slab? Taking tributary area would overestimate loads in outer columns and underestimate loads in interior columns.
However, ACI 315R-11 (which is limited to 5 story buildings) states: 9.9.1 Vertical reactions at columns and walls - Vertical reactions of the supporting members, Ru, should be determined as the total factored design load qu multiplied by the area bound by panel centerlines around the supporting member (Fig. 9.6.1). Maybe since it's limited to low rises, the "error" is within acceptable limits. But I have to design a 10 story building with lots of transfer slabs.
However, ACI 315R-11 (which is limited to 5 story buildings) states: 9.9.1 Vertical reactions at columns and walls - Vertical reactions of the supporting members, Ru, should be determined as the total factored design load qu multiplied by the area bound by panel centerlines around the supporting member (Fig. 9.6.1). Maybe since it's limited to low rises, the "error" is within acceptable limits. But I have to design a 10 story building with lots of transfer slabs.