Column size depending on beam depth 1

Status
Not open for further replies.

pxsm

Civil/Environmental
Sep 5, 2019
4
I remember reading/hearing somewhere that in a seismic region the size of a concrete column shouldn't be smaller than the depth of the beams connected to that column or something like that. Is this stated in the ACI? If so, where? because I can't find it. I can't remember where I read/heard this so maybe this is stated in a different code or maybe my memory fails me.
Thanks
 
Replies continue below

Recommended for you

For special moment frames, see ACI 318 Section 18.7.3. The flexural strength of the columns needs to be 20% greater than the flexural strength of the beams to avoid forming a story collapse mechanism.
 