Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Combined footing quick question,

Status
Not open for further replies.

engrnmc

Structural
Apr 13, 2014
16
HK
Hi guys,

i was trying to design a combined footing, and i notice that the reaction that im getting due to seismic is positive in one column and negative in the other ( due to the direction of the siesmic, in reverse if the direction is changed). since they have a couple reaction due to siesmic sizing the footing is impossible i'll be getting trapezoidal in siesmic and if checked in static condition i'll be getting rectangular combined. i know that siesmic is instantaneous reaction and im thinking of using both the positive reaction from both the column irregardless of the direction. but i hope someone could in lighten me. i cant find a good sample dealing with siesmic combined footing.

thanks
 
Replies continue below

Recommended for you

If you've got one column in uplift, I wouldn't be attempting to apply the conventional combined footing methods. I'd look at each load case independently and work out a first principles solution for each. Your uplift case will be quite different from your all downwards load cases with regard to punching shear and mid-span positive moment. Depending on the strategy that you're employing, you might also need significant footing mass just to hold the uplift column down.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Then how would you design a footing that causes an uplift reaction on one column? And even if its not an uplift. most one the time reaction from dynamic will cause either a much small reaction at one column or an uplift, in my case an uplift, compared to static which will have a reaction almost the same, if reareaction loads are the same proportionally from the two column.
 
I'd design it for each load case using first principles. Often, a combined footing only works when a substantial portion of one or both column loads is present. If there are load cases where that is not true, or there are load reversals, you need to keep a close eye on them.

If you post some sketches showing the load cases that you're considering and how you're proposing to handle them, I'd be happy to provide comment.



I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
I agree with KootK, I think. I would design the combined footing for the gravity cases, then add enough mass or tiedown resistance at each column to overcome the seismic uplift.
 
thats kinda my problem

thanks alot from your inputs, i tried to design the size of the combined footing considering static case and applying the said size to dynamic causing a great amount of eccentricity causing it to failing in the allowable bearing capacity even considering 130% increase in the allowable. Non the less i think i don't have any choice but to satisfy both static and dynamic.

thanks again,
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Top