Can anyone advise me if it is acceptable practice to combine Lab Extract or General Ventilation duct, with an LEV exhaust duct?
I'm conducting a review of proposed LEV installations in a new Hospital under construction, and most of the exhaust ducts for the various LEV's appear to take additional connections from lab extract ducts and in some cases from general ventilation extract.
I've checked all the regs I can find including information in HTM 03-01, HSG 258, NFPA 45 & 91, SMACNA, ANSI/AIHA Z9.5, OSHA and ASHRAE and as detailed as these regs all appear to be, none of them addresses this question.
LEV's I've dealt with in the past had dedicated exhaust ductwork and fan installations with no additional connections to either lab extract or general ventilation. Common sense tells me this is wrong because of the potential for cross contamination, but as the old adage goes - 'never assume, check!'
In the absence of hard evidence that the installations are non compliant, I'll be unable to flag the concern.
I'm conducting a review of proposed LEV installations in a new Hospital under construction, and most of the exhaust ducts for the various LEV's appear to take additional connections from lab extract ducts and in some cases from general ventilation extract.
I've checked all the regs I can find including information in HTM 03-01, HSG 258, NFPA 45 & 91, SMACNA, ANSI/AIHA Z9.5, OSHA and ASHRAE and as detailed as these regs all appear to be, none of them addresses this question.
LEV's I've dealt with in the past had dedicated exhaust ductwork and fan installations with no additional connections to either lab extract or general ventilation. Common sense tells me this is wrong because of the potential for cross contamination, but as the old adage goes - 'never assume, check!'
In the absence of hard evidence that the installations are non compliant, I'll be unable to flag the concern.