- Nov 14, 2017
- 7
We are working on a new project in a low seismic area (SDC B) with proposed precast concrete columns in the front of the facility. The proposed lateral system will be precast concrete columns in combination with joist girders/joists used as moment frames.
From Table 12.2-1 out of ASCE 7-10 the design coefficients and factors for seismic force-resisting systems are:
• C.7 Ordinary reinforced concrete moment frames with an R=3
• H Steel systems not specifically detailed for seismic resistance with an R=3
Is there anything in IBC 2015/ASCE 7-10 that would disallow this? From my research it looks like this is allowed per "12.2.3 Combinations of Framing Systems in the Same Direction" as long as we use the worst case requirements of each individual system.