Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Commercial Addition at what SF is a sprinkler system required?

Status
Not open for further replies.

TwBryant

Mechanical
Apr 27, 2010
3
An older Bar wants to add an addition to the bar that also will be used as a bar. The existing Bar is about 1,200 SF. How many square feet can be added to this bar before a fire sprinkler system is required?
 
Replies continue below

Recommended for you

Depends where you are and what the in-force building codes require.
 
Okay, I found it...
IBC, 303.1, Group A, A-2, Bars.

IBC 903.2.1.2 Group A-2 [F] fire sprinklers are required if...
The fire area exceeds 5,000 SF,
The fire area has an occupant load of 100 or more,
The fire area is located on a floor other that the level of exit discharge.

and

IBC Table 1004.1.1 states that with standing room only the floor area in SF per occupant is 5 net or with tables and chairs the floor area in SF per occupant is 15 net.

Now if that is not confusing, now the Bar Owner has some thinking to do.

If anyone has anything to add, please do so!
 
It sounds like you answered your own question. Make sure you under the intent of fire area, especially if this is a mixed-use building.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor