I have searched the site and have come up empty. Any help would be appreciated as I would like some opinions on how to properly size the airflow to the situation below.
An island kiosk type structure is to be built in the middle of a large open room. The owner wants the room to be able to cook and prepare food, so of course there are fryers and possibly some convection ovens. The code allows for a recirculating system, as since this kiosk is in the middle of the room with no good way of routing exhaust duct, an normal kitchen exhaust system is not allowed.
Per the code, "Factory-built commercial cooking recirculating systems" shall not be required to comply with exhaust code requirements. "Spaces in which these systems are located shall be considered to be kitchens and shall be ventilated" per ventilation table. "For the purpose of determining the floor area required to be ventilated, each individual appliance shall be considered as occupying not less than 100 sq. ft."
Now the ventilation table for kitchens only includes an exhaust flow rate, and using that last line of the code (2 fryers, 2 convection ovens) the square footage to determine airflow shall be 400 sq. ft. (though the actual space is less than that). At 0.7 cfm per sq. ft. required exhaust, 280 cfm is required. But with this being a recirc hood system, is this now the required OA?
This is where I'm getting hung up. The code states that recirc hood systems don't need to exhaust the air, but the ventilation schedule requires it. Does this code allow for indirect exhaust? Where the hood doesn't need to be exhausted but the room does?
Another problem arises with getting supply air to the room. An electrical closet in this space is situated away from the wall too, but a supply fan blows air from the building into the space, in an indirect supply fashion. Is this a possibility for supplying air into the kitchen?
I'm at the beginning of the design and am looking for some people with experience that may be able to help or offer solutions that I haven't thought of yet. The space is located in Michigan, and while they have their own code, it is based off of IMC 2012.
An island kiosk type structure is to be built in the middle of a large open room. The owner wants the room to be able to cook and prepare food, so of course there are fryers and possibly some convection ovens. The code allows for a recirculating system, as since this kiosk is in the middle of the room with no good way of routing exhaust duct, an normal kitchen exhaust system is not allowed.
Per the code, "Factory-built commercial cooking recirculating systems" shall not be required to comply with exhaust code requirements. "Spaces in which these systems are located shall be considered to be kitchens and shall be ventilated" per ventilation table. "For the purpose of determining the floor area required to be ventilated, each individual appliance shall be considered as occupying not less than 100 sq. ft."
Now the ventilation table for kitchens only includes an exhaust flow rate, and using that last line of the code (2 fryers, 2 convection ovens) the square footage to determine airflow shall be 400 sq. ft. (though the actual space is less than that). At 0.7 cfm per sq. ft. required exhaust, 280 cfm is required. But with this being a recirc hood system, is this now the required OA?
This is where I'm getting hung up. The code states that recirc hood systems don't need to exhaust the air, but the ventilation schedule requires it. Does this code allow for indirect exhaust? Where the hood doesn't need to be exhausted but the room does?
Another problem arises with getting supply air to the room. An electrical closet in this space is situated away from the wall too, but a supply fan blows air from the building into the space, in an indirect supply fashion. Is this a possibility for supplying air into the kitchen?
I'm at the beginning of the design and am looking for some people with experience that may be able to help or offer solutions that I haven't thought of yet. The space is located in Michigan, and while they have their own code, it is based off of IMC 2012.