Hi All,
I am a professional engineer in FL and do Structural & MEP. Full disclosure I do not usually get into 3 phase electrical these normally sub out to electrical engineers I work with. In this case I am doing a tenant buildout in a commercial space which is a standard single phase 200 amp system which I have done plenty. But it turns out the space does not have 200 amp service, only 100 amp and the main distribution panel is 600 amps 3 phase. Now I need to do an upgrade on a 3 phase and already bid out the project, and due to budget and time constraints I am trying to do this myself if I can make sense of it.
Anyways, this space now needs an upgrade. The existing panel setup is as follows: (see attached for riser layout)
600amp 3 phase panel feeding 6 sub panels for each tenant space.
(4) 200 amp panels
(2) 100 amp panels
This panel is one of the 100 amps that needs to be upgraded to 200 amp.
My questions are as follows:
- Right now this whole system in my opinion needs an upgrade. I usually do using 80% capacity (as a rule of thumb) of the system I should have (5x200)+100 = 1100*0.8 = 880 therefore either 800 or 1000 amp service is require at least. I do not necessarily want to get in doing load calcs for all of these units. If the city requests it then we got to do it, but I do not want to be the one to suggest it. Should I simply call out for a 1000 amp panel and call out the appropriate wire and conduit size and then let the utility figure out the rest? I can handle this.
-OR since this is a 3 phase panel (btw does not look like the 3rd leg is being utilized in any of the sub panels) require a more complicated calculation? Is there a guideline in NEC or others that I should follow in this situation?
Thanks in advance for the assistance!
I am a professional engineer in FL and do Structural & MEP. Full disclosure I do not usually get into 3 phase electrical these normally sub out to electrical engineers I work with. In this case I am doing a tenant buildout in a commercial space which is a standard single phase 200 amp system which I have done plenty. But it turns out the space does not have 200 amp service, only 100 amp and the main distribution panel is 600 amps 3 phase. Now I need to do an upgrade on a 3 phase and already bid out the project, and due to budget and time constraints I am trying to do this myself if I can make sense of it.
Anyways, this space now needs an upgrade. The existing panel setup is as follows: (see attached for riser layout)
600amp 3 phase panel feeding 6 sub panels for each tenant space.
(4) 200 amp panels
(2) 100 amp panels
This panel is one of the 100 amps that needs to be upgraded to 200 amp.
My questions are as follows:
- Right now this whole system in my opinion needs an upgrade. I usually do using 80% capacity (as a rule of thumb) of the system I should have (5x200)+100 = 1100*0.8 = 880 therefore either 800 or 1000 amp service is require at least. I do not necessarily want to get in doing load calcs for all of these units. If the city requests it then we got to do it, but I do not want to be the one to suggest it. Should I simply call out for a 1000 amp panel and call out the appropriate wire and conduit size and then let the utility figure out the rest? I can handle this.
-OR since this is a 3 phase panel (btw does not look like the 3rd leg is being utilized in any of the sub panels) require a more complicated calculation? Is there a guideline in NEC or others that I should follow in this situation?
Thanks in advance for the assistance!