Does anyone have a link to a table or info which shows the common causes of faults in power stations?
 
Replies continue below

Recommended for you

What exactly are you asking for? There are many faults ranging from a fault in a generator stator to faults on the feeds of auxiliary systems or even lighting. One could even assume a power station operator error is a fault.
You need to be more specific.
 
Yea, thanks for reminding. For example I have a table in front of me that look something like this:

Cause of overhead-line faults, British system 66kV and above:

faults/160km of line/year
lightning 1.59
dew,fog,frost 0.15
snow, ice 0.01
gales
salt spray
Total

so on...

it will be great if i can find a table that looks something like the above.

Thanks
 
I don't have a table, but the the majority of our substation faults are animal related with snakes being the worst and birds second.
 