Dear All,
for a system have 2+1 standby PSVs with staggered arrangement as per ASME U-134. the first PSV is set at MAWP and the second is set 105% MAWP. Bot PSVs have a common inlet from the vessel which will be designed as per API 520 PII such that the area of this inlet pipe shall be at least equal to the sum of the inlet flange area of the twp PSVs i.e. section 5.2 and such that PSV inlet non-recoverable losses of 3% of pressure drop is not exceeded.
For the sizing of the individual PSVs, the rated capacity of each will be used for calculating the outlet pipe such that the area of the outlet individual pipe is also equal to or greater than the outlet flange area of the PSV. However, if the two outlets combine into a common collection tail pipe before joining the main flare subheader/header.. what should be the capacity basis for that common collection pipe backpressure estimation and hence its sizing:
a- the maximum rated capacity out of the two knowing that rated capacity is a function of the overpressure of the PSV and its set pressure.
b- the sum of the rated capacity of both of the PSVs even if the opening is sequential. We understand that when PSV opens it goes to full lift at its rated capacity as long as the bore area exceeds 1/4 of the nozzle diameter. Is therefore required to consider both rated capacity of both of the operating PSVs since Engineer can't have assurance of the set pressure tolerances of the second PSV and whether it would sequentially open following the sudden full lift opening of the first PSV?? Do you think that option b is clarified by API 521 section 4.9.4.3 of the need to have an aggregate flow consideration irrespective to the staggering due to the above mentioned tolerances
thanks
Regards,
for a system have 2+1 standby PSVs with staggered arrangement as per ASME U-134. the first PSV is set at MAWP and the second is set 105% MAWP. Bot PSVs have a common inlet from the vessel which will be designed as per API 520 PII such that the area of this inlet pipe shall be at least equal to the sum of the inlet flange area of the twp PSVs i.e. section 5.2 and such that PSV inlet non-recoverable losses of 3% of pressure drop is not exceeded.
For the sizing of the individual PSVs, the rated capacity of each will be used for calculating the outlet pipe such that the area of the outlet individual pipe is also equal to or greater than the outlet flange area of the PSV. However, if the two outlets combine into a common collection tail pipe before joining the main flare subheader/header.. what should be the capacity basis for that common collection pipe backpressure estimation and hence its sizing:
a- the maximum rated capacity out of the two knowing that rated capacity is a function of the overpressure of the PSV and its set pressure.
b- the sum of the rated capacity of both of the PSVs even if the opening is sequential. We understand that when PSV opens it goes to full lift at its rated capacity as long as the bore area exceeds 1/4 of the nozzle diameter. Is therefore required to consider both rated capacity of both of the operating PSVs since Engineer can't have assurance of the set pressure tolerances of the second PSV and whether it would sequentially open following the sudden full lift opening of the first PSV?? Do you think that option b is clarified by API 521 section 4.9.4.3 of the need to have an aggregate flow consideration irrespective to the staggering due to the above mentioned tolerances
thanks
Regards,