Communication manhole grounding

Status
Not open for further replies.

mel127

Electrical
Dec 13, 2007
27
Is GROUNDING necessary for Communication manholes(concrete type)?
Thanks in advance.
 
Replies continue below

Recommended for you

That's normally specified by the owner's standards. Typically yes. What type of communication cabling?
 
If the covers are metal, they may need to be grounded, per the latest NEC.
 
alehman,
the cabling is fiber optics.
 
If there is no metal sheath or jacket and no power wiring, I would say there is little need for grounding. If the cable has a metal sheath that is exposed in the manhole, telco's typically will want it to be grounded in some manner
 