Communication Tower

Status
Not open for further replies.

bobziva

Electrical
May 7, 2003
41
The couple answars I have to prepare from Communication Engineering, what is not my branch, i.e. from the Construction of Antenna Communication Tower.
(1)Lightning Protection of the Tower
(are special requirements provided by Codes, Standards?)
Any material available on the internet ?
(2)Grounding the Tower
(are special requirements provided by Codes, Standards ?)
Any material on the internet ?
(3)230 kV Transmission Line is located very close to the
future tower. How far can be ?
Thanks
 
Replies continue below

Recommended for you

I repeat the question :

The Communication Tower ( 80 ft) must be grounded and protected from the lightning. Is it the same as for the building ? What about 230 kV transmission line passing close to the tower. How far it can be ?
Tnank you for the help. Any text on the internet ?
 
Motorola has a telecommunication site standard called R56. It's had to find. Also, checkout Polyphaser's web site or call them. Checkout the Tech Info tab.

Grounding is a must. There are different theories on grrounding. Lookup Ufer grounding (foundation) and halo grounds (insidee shelters).
I have to run if I have time I come back to add more.

photistor
 