cycloneengineer
Structural
- Aug 18, 2022
- 2
Hi,
Regarding Component and Cladding wind pressures as defined in ASCE 7-10: Do the positive and negative pressures on a wall component get combined? For example, I have a girt with a trib. area of ±20sf. The calculated C&C pressures (Zone 4) are: +21.2psf and -25.4psf.
Note 3 on Figure 30.4-1 defines the positive and negative values as pressures that act towards and away from the surface. Where I get confused is Note 4, which says "Each component shall be designed for maximum positive and negative pressures." Do you take this to mean combining the pressures or as two separate cases?
If they are to be combined, would you combine them as:
(a) 21.2psf + (-25.4psf) = -4.2psf or
(b) 21.2psf - (-25.4psf) = 46.6 psf
Attached is a picture of how I'm envisioning the wind pressures to act. Thanks!
Regarding Component and Cladding wind pressures as defined in ASCE 7-10: Do the positive and negative pressures on a wall component get combined? For example, I have a girt with a trib. area of ±20sf. The calculated C&C pressures (Zone 4) are: +21.2psf and -25.4psf.
Note 3 on Figure 30.4-1 defines the positive and negative values as pressures that act towards and away from the surface. Where I get confused is Note 4, which says "Each component shall be designed for maximum positive and negative pressures." Do you take this to mean combining the pressures or as two separate cases?
If they are to be combined, would you combine them as:
(a) 21.2psf + (-25.4psf) = -4.2psf or
(b) 21.2psf - (-25.4psf) = 46.6 psf
Attached is a picture of how I'm envisioning the wind pressures to act. Thanks!