Composite Deck T&S Reinforcement Placement

Status
Not open for further replies.

engjg

Structural
Jan 2, 2015
96
Anyone aware of code requirements or industry recommendations on placement of temperature and shrinkage steel WWR for composite deck. SDI seems to defer to CRSI but I can't seem to find any document from them that addresses.
 
Replies continue below

Recommended for you

Shouldn't your T&S reinforcement be considered top reinforcement in that situation to minimize crack width at the expose face?
 
If you look at the SDI Standard for Composite Floor Deck (ANSI/SDI-C1.0) it states that welded wire reinforcement or bars should have a minimum area of 0.00075 x Concrete Area above the deck (per foot) but not less than 6x6-W1.4xW1.4. Suggested 3/4" to 1" clear from the top.

They also state that fiber reinforcement can be used as well.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
Thanks JAE. I found it it the 2006 version of the that document but it appears they removed it in the 2017? How often do you see WWR draped in practice?
 
Never

Check out Eng-Tips Forum's Policies here:
faq731-376
 
If 3/4" or 1" is recommended industry practice...it seams like the FDDM design examples for concentrated load evaluation of weak axis bending distribution steel is out-of-sync... as they assume 1/2 the slab depth placement.

For a common 3"slab over 2"deck w/ minimum T&S WWR, a d=0.75" vs. d=1.5" yields a significant difference in capacity...
 
engjg,
We typically show the WWF in the center or at least a bit above the center of the net slab thickness (that portion above the top of the flutes).

We also call for #4 bars, about 4 ft. long or so, oriented perpendicular to the major interior girder beams as you typically get flexural induced cracks along those beams.

Don't ever drape WWF although I suppose if you emphasized it on your plans, showed exactly how to chair it, etc. you might get a contractor that would properly perform for you.



Check out Eng-Tips Forum's Policies here:
faq731-376
 