Haldorson, It's obvious it's something I never looked at closely because I've never encountered TJI construction in anything but an 13R system.
I'm learning, Georgia just adopted the 2013 edition of NFPA #3 on January 15th this year making the jump from
2002. Eleven years, I suppose it is about time. I have my new copy of the 13 handbook and I read a few pages each night. Lots of exciting new stuff to learn!
8.15.1.2.8 "provided that in composite wood joist construction the joist channels are firestopped into volumes each not exceeding 160 ft3 (4.53 m3) to the full depth of the joist
with material equivalent to the web construction, shall not require sprinkler protection." I am a newbie here but if I am reading this correctly it can be fire stopped with 1/2" plywood if the web is 1/2" as long as we use the same grade plywood?
But even if it is fire stopped we're looking at the dreaded 3,000 sq ft. if I am reading this correctly.
Oh, I got it....
"Light or ordinary hazard occupancies where noncombustible or limited-combustible ceilings are attached to the bottom of composite wood joists either directly or on to metal channels not exceeding 1 in. (25.4 mm) in depth, provided the adjacent joist channels are firestopped into volumes not exceeding 160 ft3 (4.5 m3) using materials equivalent to 1⁄2 in. (12.7 mm) gypsum board and at least 31⁄2 in. (90 mm) of batt insulation is installed at the bottom of the joist channels when the ceiling is attached utilizing metal channels."
It's apparent I have some reading and catching up to do. Be back in a few days when I know what I am talking about