Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Compressor chillers or Absorption chillers 1

Status
Not open for further replies.

SPLIT

Mechanical
Dec 21, 2002
57
I would like to know if 400t absorption chiller is competitive if using 40°C waste water, to chill water at 5°C
 
Replies continue below

Recommended for you

Dear friend,
what is the ambient temperature of the chiller location?
I don't thick this 40 deg temperature is enough to run the chiller system!

KMPillai
 
Hello SPLIT!

May i suggest you to direct your question, which is an interesting one, to the HVAC/REFRIGERATION FORUM. I think, there you will find quite more fellows willing to answer.
I 'll do that there, as well.
zzzo


 
I think the Yazaki absorption chillers require at least 95C fluid to effectively chill, using lithium bromide, and at that point their COP is only about 1.

 
Hi!
To Davefitz: From your knowledge/experience what you have to say about absorption chillers, in particular those lithium bromide requiring hot water at lower temperatures at the level of the generator(of course you have to consider a bigger one, as well the absorsor!) around 70~75 ºC (or 158~167 ºF). The idea is to combine/integrate this system in multi-task/uses solar installations.
zzzo
 
Hi SPLIT!

I don't think so! We still having a lots of problems to stabilize the cycle with temperatures around 60~70 ºC and COP ~ 0.45 to 0.55 For temperatures around 40 ºC, you can consider it that as a pre-heating step, at the most. But than again, the COP will be lower, in order to reach the required temperatures at the generator.
Mac
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor