SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
This is what the attic space looks like and it covers approximately 5,600 sq ft.
Wet system. Yes, there is insulation but it is more for air conditioning as the building sits on the Florida/Georgia state line. Flat roof with 2"x8" top and bottom chords having 2"x4" diagonals.
Anyone know of any really small fitters looking for a job?
Looking at the Tyco Model CC2 — 4.2 and 5.6 K-factor Combustible Concealed Space Sprinklers™ Specific Application, Upright sprinklers and I have a couple questions.
Looking at Figure 7 (that is the closest to what we have) on pdf page 6 (I will be using steel pipe) we see a 2" maximum and 1 1/2" minimum distance from deflector to bottom of top chord on the sprig up sprinkler but there's a second sprinkler on the pie itself positioned much lower.... why? The way I read it we're safe if we run the deflectors 2" to 1 1/2" down but...
Another question I have has to do with "blocking".
Ok, what is this "blocking" they are speaking of? I know what the baffle is but now blocking? I got to go back and check but I don't think I have seen a "blocking" requirement for any of the other (Viking) concealed space sprinklers but I can not be sure.
Non combustible blocking... or since the joist is combustible I can use wood? Same wood as I use in the baffle?
I am thinking of running all the pipe below the drywall, there is a suspended ceiling below that, using 1" sprig-ups to supply each concealed space sprinkler. What I would do is cut a 2'x2' hole in the drywall, install my sprinkler head on a sprig up and have reinstall the drywall around it with tape and fire stopping. I know I sure can't fit in the space.
Now I am gonna go read Vikings and see if they got "blocking" requirements.
Wet system. Yes, there is insulation but it is more for air conditioning as the building sits on the Florida/Georgia state line. Flat roof with 2"x8" top and bottom chords having 2"x4" diagonals.
Anyone know of any really small fitters looking for a job?
Looking at the Tyco Model CC2 — 4.2 and 5.6 K-factor Combustible Concealed Space Sprinklers™ Specific Application, Upright sprinklers and I have a couple questions.
Looking at Figure 7 (that is the closest to what we have) on pdf page 6 (I will be using steel pipe) we see a 2" maximum and 1 1/2" minimum distance from deflector to bottom of top chord on the sprig up sprinkler but there's a second sprinkler on the pie itself positioned much lower.... why? The way I read it we're safe if we run the deflectors 2" to 1 1/2" down but...
Another question I have has to do with "blocking".
Pdf Page 3 said:for solid wood joist construction (Fig. 5)and obstructed wood truss construction (Fig. 7), [highlight #FCE94F]blocking[/highlight] must be provided in each upper deck and ceiling joist channel at a maximum 32 feet (9,75m) intervals. This blocking shall be installed to the full depth of the joists and be installed so as to not allow heat to escape through or above the blocking. The blocking must be constructed using a non-combustible material or the joist construction material
Ok, what is this "blocking" they are speaking of? I know what the baffle is but now blocking? I got to go back and check but I don't think I have seen a "blocking" requirement for any of the other (Viking) concealed space sprinklers but I can not be sure.
Non combustible blocking... or since the joist is combustible I can use wood? Same wood as I use in the baffle?
I am thinking of running all the pipe below the drywall, there is a suspended ceiling below that, using 1" sprig-ups to supply each concealed space sprinkler. What I would do is cut a 2'x2' hole in the drywall, install my sprinkler head on a sprig up and have reinstall the drywall around it with tape and fire stopping. I know I sure can't fit in the space.
Now I am gonna go read Vikings and see if they got "blocking" requirements.