KHoff
Structural
- Aug 20, 2013
- 60
I designed an auto repair shop that is intended to have vehicular lifts installed on the slab on grade. The lifts consist of two vertical columns with a horizontal beam rigidly attached at the top. The columns have arms that swing under the vehicle and lift it. The concentrated load from one of the columns is approximately 7 kips when the lift is at max capacity. The slab is 5" thick with #3 bars at 12" on center each way. Seems to me the 7 kip load is a relatively light load for this slab to support.
The lift manufacturer has indicated they do not recommend the columns be installed within 36" of a crack in the slab. In this case, there is a control joint within 36" (about 12" from the column). The control joints are detailed to be saw cut with a depth of 1/4 the slab thickness. Reinforcing is continuous through the joint. I am looking for input on if the manufacturer's concerns are justified. I might be more concerned with a heavier load, but I'm not sure a 7 kip load warrants making modifications to the newly constructed slab. Obviously the owner would prefer not have to do anything to the slab.
Are there any references I could use to quantify a slab capacity for a concentrated load adjacent to a control joint? Also, I feel that it might be conservative to assume the load is at a slab edge since reinforcing is continuous through the joint. I appreciate any input.
The lift manufacturer has indicated they do not recommend the columns be installed within 36" of a crack in the slab. In this case, there is a control joint within 36" (about 12" from the column). The control joints are detailed to be saw cut with a depth of 1/4 the slab thickness. Reinforcing is continuous through the joint. I am looking for input on if the manufacturer's concerns are justified. I might be more concerned with a heavier load, but I'm not sure a 7 kip load warrants making modifications to the newly constructed slab. Obviously the owner would prefer not have to do anything to the slab.
Are there any references I could use to quantify a slab capacity for a concentrated load adjacent to a control joint? Also, I feel that it might be conservative to assume the load is at a slab edge since reinforcing is continuous through the joint. I appreciate any input.