Concentrated wheel loads on steel checker plate 1

Status
Not open for further replies.

victory732

Structural
Jun 7, 2005
1
Anyone know of an industry standard for designing steel "checker" plate for large concentrated wheel loads such as imposed by hard rubber tire fork lifts? AISC gives load tables for uniform distributed loads only. What trib width of plate should be assumed to carry the load?
 
Replies continue below

Recommended for you

Consider Roark's Formula's for Stress and Strain, Table 26, Case 1c. This gives stresses for a flat plate with a uniform patch load. If you don't satisfy those conditions then you can perform a yield line analysis. From my class notes in college for concrete design my professor stated the following. Note this is for concrete but I would assume steel would be close. You will have to be certain to check shear.

"The effective width of a slab which will participate in carrying the load can be obtained as follows. The effective width is the smallest of b1+5h, b1+4/3*x1, or b1+2/3*ln. If the load is at the edge of the slab use b1 plus 1/2 the additional width given above."

ln = clear span of slab between beams
b1 = width of patch load perpendicular to span
x1 = distance from edge of patch load to nearest supporting beam
h = thickness of slab

AISC 9th edition has design information for floor plate on page 2-145. You may also review previous post on concentrated loads on slabs.
 
victory732,

I don't have much to add except that I use the Roark's Table 26 Case 1c for this type of calculation also. Just thought I'd stop in to second aggmans's post.

-Mike
 
I would check into some Manufacturer's catalogs. The Ohio Grating Catalog has some useful info on wheel loads and contact areas for fork lift loads, under Heavy Duty Steel Design Criteria. For gratings, they suggest a deflection limit of L/400.
 
I used to have a table with allowable uniform loads and concentrated loads on floor plates. I have used it for years with great success. I will search for it and if you let me know, I would e-mail you a copy.

It is based on plate theory and boundary conditions at all four edges.

Good luck


Lutfi
 