P1ENG
Structural
- Aug 25, 2010
- 237
I'll admit that concrete knowledge is the weakest amongst building materials, so I only get involved in very simple concrete things. Well, I am being asked for a letter of approval for the concrete used in sonotube piers used for bearing and lateral resistance of a single-story modular building. The piers have weld plates for anchoring the building and are only 4' deep on the East coast (Mass). So freeze/thaw is expected. The drawings specify 4,000 psi and 6% +/- 1.5% air content. I received documents of (2) samples which tested (3) cylinders each. One sample says that % air (T152 or T196) is 3.0% and has 28 day strengths of 6250, 6050, and 6150 psi. So the air is lower than specified but the strength is higher than required. The other sample meets strength and air specs. Is there some way to decrease the required air because of the extra strength in the concrete? If not, what is my next step? I've already stated that I can't write the letter because the concrete that was produced was observed to not meet the specifications and that I would only write a letter if all involved were made aware of the missed specification and if the concrete producer provide written acceptance of liability for issues caused by freeze/thaw cycles. That is unless there is another avenue...
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant
Juston Fluckey, SE, PE, AWS CWI