BadgerEngineer
Structural
- Sep 16, 2008
- 43
We often get asked by contractors if its acceptable to pour deep concrete beams in two pours. This usually occurs when the slab ties into the side of the beam. (Top of slab elevation is lower than top of beam elevation) And GC wants to pour the slab to outside edge of beam in one pour.
Is this something others are allowing? Typically we do not, however, this has been met by much resistance.
If you were to allow a cold joint in a concrete beam - what is the primary failure mode that you'd need to check. I understand longitudinal shear at the cold joint may be an issue. However, if the hooks are embedded in the lower section of the beam you will have rebar continually crossing the cold joint. In addition, the concrete can be left rough at both faces. Concrete friction and your #3 hooks (or similar) should provide enough strength to resist this load.
Another issue for exterior beams may be water penetration - if a cold joint is left in the beam, water could easily find its way into the beam and corrode the rebar.
Does anyone have any references or design suggestions for me on this topic? What should I be checking to approve this method?
I greatly appreciate your input.
Is this something others are allowing? Typically we do not, however, this has been met by much resistance.
If you were to allow a cold joint in a concrete beam - what is the primary failure mode that you'd need to check. I understand longitudinal shear at the cold joint may be an issue. However, if the hooks are embedded in the lower section of the beam you will have rebar continually crossing the cold joint. In addition, the concrete can be left rough at both faces. Concrete friction and your #3 hooks (or similar) should provide enough strength to resist this load.
Another issue for exterior beams may be water penetration - if a cold joint is left in the beam, water could easily find its way into the beam and corrode the rebar.
Does anyone have any references or design suggestions for me on this topic? What should I be checking to approve this method?
I greatly appreciate your input.