I'm working on a six story concrete building (beams & columns with pan joists). I'm having difficulty coming up with a rational and efficent method of determining the worst case design loads for my columns(satifying ACI 8.8). Here's what I'm thinking of doing:
1. Full L + D all the way down.
2. Partial L + D patterns all the way down (same patterns on all floors).
3. Partial L + D alternating patterns as I go down (different patterns on alternating floors).
4. Same as (3) but switching which floors get which patterns.
This is already a substantial undertaking. In addition, I'm wondering if I need the consider the following:
1. Same as above but with no live loads applied above the floor under consideration. Perhaps this could produce the loading with the greatest moment/axial ratio (ACI 8.8.1)?
2. I must, of course, do a lateral analysis. Am I required to peform each of the combinations above in conjunction with each of my lateral load cases? I'm examining wind from four directions. Each direction comes with 4 load cases for different combinations of L+D+W. So far then, I've got 4x3=12 load cases to consider for lateral + full live and dead load. Now...do I have to consider each individual load pattern in combination with the lateral loads??? That would yield 12x4 = 48 separate load cases!! I think that there must be a better way.
3. How do I apply live load reduction factors to the column moments? In a moment frame structure it is diffcult to determine the corresponding loaded area that produces each moment. Especially when there are different magnitudes of floor loading applied to various areas of the building.
Can anyone recommend a simpler way for me approach my column design. I am using RISA 3D for the structural analysis. Thanks in advance for your help!
1. Full L + D all the way down.
2. Partial L + D patterns all the way down (same patterns on all floors).
3. Partial L + D alternating patterns as I go down (different patterns on alternating floors).
4. Same as (3) but switching which floors get which patterns.
This is already a substantial undertaking. In addition, I'm wondering if I need the consider the following:
1. Same as above but with no live loads applied above the floor under consideration. Perhaps this could produce the loading with the greatest moment/axial ratio (ACI 8.8.1)?
2. I must, of course, do a lateral analysis. Am I required to peform each of the combinations above in conjunction with each of my lateral load cases? I'm examining wind from four directions. Each direction comes with 4 load cases for different combinations of L+D+W. So far then, I've got 4x3=12 load cases to consider for lateral + full live and dead load. Now...do I have to consider each individual load pattern in combination with the lateral loads??? That would yield 12x4 = 48 separate load cases!! I think that there must be a better way.
3. How do I apply live load reduction factors to the column moments? In a moment frame structure it is diffcult to determine the corresponding loaded area that produces each moment. Especially when there are different magnitudes of floor loading applied to various areas of the building.
Can anyone recommend a simpler way for me approach my column design. I am using RISA 3D for the structural analysis. Thanks in advance for your help!