Nor Cal SE
- Mar 7, 2017
- 84
I am plan reviewer and have a situation where an engineer has submitted a typ detail for a vertical conduit passing through a stud wall sill plate and concrete curb below at a typical exterior strip footing condition. As part of the detail, the designer shows the normal longitudinal reinforcing bar in the curb bending around the conduit stating 3/4" min concrete cover at this location. Clearly this does not meet ACI 318-14's minimum concrete cover for bars exposed to weather. However, should I consider this acceptable since the 3/4" cover occurs only at a very localized area, plus this is primarily temperature/shrinkage steel? Apart from the conduit condition, the details show the rebar running down the center of the curb as you'd expect; ample concrete cover. If I enforce 1-1/2" min concrete cover even at the conduit, I expect the designer will complain about how this will restrict potential conduit sizes.
