Hi there,
I need to design a house-keeping pad for an air handling unit.
The mechanical engineer stated that the depth of the pad can be 4" thick.
The floor load where we will be putting these pads has a design live load of 100psf, so I am trying to make sure that the pressure from the pad and AHU do not go above this.
The AHU is around 1650 lbs. I applied a dead load safety factor to the AHU and pad load. In order to make the factored pressure less than 100 psf, I needed to increase the house keeping pad plan area to 1'4" around the AHU.
However, I am not sure if I can consider this full plan areas as spreading the load? Is there a point where the additional plan area contribution will not spread the load?
I drew a 45 degree angle line in red from the edge of the AHU (assuming this is the way the load will spread from the AHU). Which of the three lengths can I assume to spread the load? See below sketches :
First sketch shows the plan area :
Second sketch shows the section :
I believe I will run into some issues if I can't consider the full pad width, as the factored pressure with this load is ~ 100 psf.
Any help would be appreciated.
I need to design a house-keeping pad for an air handling unit.
The mechanical engineer stated that the depth of the pad can be 4" thick.
The floor load where we will be putting these pads has a design live load of 100psf, so I am trying to make sure that the pressure from the pad and AHU do not go above this.
The AHU is around 1650 lbs. I applied a dead load safety factor to the AHU and pad load. In order to make the factored pressure less than 100 psf, I needed to increase the house keeping pad plan area to 1'4" around the AHU.
However, I am not sure if I can consider this full plan areas as spreading the load? Is there a point where the additional plan area contribution will not spread the load?
I drew a 45 degree angle line in red from the edge of the AHU (assuming this is the way the load will spread from the AHU). Which of the three lengths can I assume to spread the load? See below sketches :
First sketch shows the plan area :
Second sketch shows the section :
I believe I will run into some issues if I can't consider the full pad width, as the factored pressure with this load is ~ 100 psf.
Any help would be appreciated.