Does any one could advise the resitivity value of concrete for an indoor substation.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
The floor slab of an indoor substation is not completely buried, and may be isolated by a vapor barrier. The steel mesh reinforcing will keep the floor slab at essentially the same potential. The steel mesh could be modelled as a buried metal structure within the concrete. It would be easier and more conservative to model the reinforcing as an isolated buried metal structure in the upper layer of soil. This will probably show that step and touch potentials within the building are acceptable.Buried in soil, a concrete block behaves as a semiconducting medium with a resistivity of 30-90 ohm·m.