EireChch
Geotechnical
- Jul 25, 2012
- 1,300
Hi all,
The project is a retrofit of an existing 12.8m high x 48.9m dia tank supported on a 0.45m wide 2.3m deep ring foundation. Due to the retrofitting there will be an increase in loads. I am doing a check to confirm the existing reinforcement provided is sufficient. This involves revising the existing structural calcs.
Due to the additional line load, the vertical reinforcing req'd is 0.02% which is well below that ACI318 min of 900mm2 (0.2%) that has been provided. No issues there.
However, due to the additional hoop stress, resulting from the increased surcharge acting above the ringwall, we are above the allowable tensile stress of the 35MPa concrete 3.43N/mm[sup]2[/sup]> 3.29N/mm[sup]2[/sup].
I am still satisfying the maximum crack width of 0.3mm from ACI-244
Maybe I am not understanding the structural theory between load transfer between concrete and steel but the calculation approach seems flawed as the entire hoop stress is applied to the concrete alone without considering the reinforcement. Wouldn't there be some load taken by the reinforcement?
In short I am looking for a way to make this work, within the codes and rules of course.
Any help appreciated.
The project is a retrofit of an existing 12.8m high x 48.9m dia tank supported on a 0.45m wide 2.3m deep ring foundation. Due to the retrofitting there will be an increase in loads. I am doing a check to confirm the existing reinforcement provided is sufficient. This involves revising the existing structural calcs.
Due to the additional line load, the vertical reinforcing req'd is 0.02% which is well below that ACI318 min of 900mm2 (0.2%) that has been provided. No issues there.
However, due to the additional hoop stress, resulting from the increased surcharge acting above the ringwall, we are above the allowable tensile stress of the 35MPa concrete 3.43N/mm[sup]2[/sup]> 3.29N/mm[sup]2[/sup].
I am still satisfying the maximum crack width of 0.3mm from ACI-244
Maybe I am not understanding the structural theory between load transfer between concrete and steel but the calculation approach seems flawed as the entire hoop stress is applied to the concrete alone without considering the reinforcement. Wouldn't there be some load taken by the reinforcement?
In short I am looking for a way to make this work, within the codes and rules of course.
Any help appreciated.