Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Concrete spalling

Status
Not open for further replies.

wailuku

Structural
Feb 14, 2003
7
What are good references on how to repair concrete for spalling? I am currently doing a project where 8" square pedestals have spalled. In some cases the rebar is exposed and have corrosion. Is spalling repair a good idea? I at first submitted a design for complete replacement but the cost was too high.

 
Replies continue below

Recommended for you

Spalling is caused by inadequate cover to reinforcement, which leads to corrosion. The products of corrosion occupy more volume than the steel, thus the oxides push the concrete away. 8" square pedestals are very small for structural concrete, therefore the reinforcement has little cover. Repair of these will likely be fruitless, resulting in repeat failures. Suggest you rethink and replace the pedestals, doing it right this time.
 
Agree with hokie66...if you repair, you'll be doing it again. If you must repair though, look at Sika Products website...they have some good info on spall repair and on corrosion mitigation.
 
I agree with hokie66 and Ron that for small elements, replacement is ususally more cost effective in the long run. For future reference, there is a lot of information on concrete repair techniques at the IRCI website (irci.org).
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor