Hey all - I'm working on the design for an underground vault to house valves for a 42" water line. It's gotten a lot more complicated than I anticipated and I'm not sure of the best way to go about designing the critical wall. Inner dimensions are 17'-4" x 10' x 9'-11" deep.
The short wall is the critical wall as it has an enormous amt of thrust. Here's what we're looking at:
surcharge load on soil above - large - aprox 5330psf (unfactored)
active soil load on wall
thrust force (due to water hammer) where pipe enters wall - 497,677# (factored)
I've designed the long wall as a plate and that went fine. I'm not sure how to design the short wall. My initial thought is to design as a small beam section (one in each direction), taking a chunk of the thrust plus the other loads? Bottom is fixed and top would be pinned.
I'm not worried about the over all sliding- I'll address that w/ wingwalls and keys. I'm just worried about the wall surrounding the pipe entrance.
Any thoughts or suggestions appreciated!
The short wall is the critical wall as it has an enormous amt of thrust. Here's what we're looking at:
surcharge load on soil above - large - aprox 5330psf (unfactored)
active soil load on wall
thrust force (due to water hammer) where pipe enters wall - 497,677# (factored)
I've designed the long wall as a plate and that went fine. I'm not sure how to design the short wall. My initial thought is to design as a small beam section (one in each direction), taking a chunk of the thrust plus the other loads? Bottom is fixed and top would be pinned.
I'm not worried about the over all sliding- I'll address that w/ wingwalls and keys. I'm just worried about the wall surrounding the pipe entrance.
Any thoughts or suggestions appreciated!