yulinios
Chemical
- Apr 9, 2004
- 41
Hi there
In a hydraulic power plant: Toshiba Generator of 48.2 MVA, Stator and Rotor insulation class F, which is air cooled, there are 4 coolers plate fin type fixed with tube sheets, the circulation of air is performed by mean of rim duct equipped on the generator rotor, the cooling system was designed to operate only with 3 coolers, with p.f. 09, and aging factor of 1.1.
There is a condensation problem in the tube sheets of the coolers, condensate water reach the floor (water box is not enough in large), we think that is very risky that water could reach the stator (vertical position) so we are drying the floor with wipes permanently by now.
Humidity has been increased by rains, relative humidity now is 55 – 60 %, dew point is 19 - 21°C , the water inlet temperature is 14 °C (cooler design: 25°C), we are decreasing the flow from 40 to 24 L/seg, condensation has decreased but the generator stator temperatures have increased in 4°C (from 84 to 88°C).
Are there some problem to operate the generator with 4°C more?
Thanks, bye there!
In a hydraulic power plant: Toshiba Generator of 48.2 MVA, Stator and Rotor insulation class F, which is air cooled, there are 4 coolers plate fin type fixed with tube sheets, the circulation of air is performed by mean of rim duct equipped on the generator rotor, the cooling system was designed to operate only with 3 coolers, with p.f. 09, and aging factor of 1.1.
There is a condensation problem in the tube sheets of the coolers, condensate water reach the floor (water box is not enough in large), we think that is very risky that water could reach the stator (vertical position) so we are drying the floor with wipes permanently by now.
Humidity has been increased by rains, relative humidity now is 55 – 60 %, dew point is 19 - 21°C , the water inlet temperature is 14 °C (cooler design: 25°C), we are decreasing the flow from 40 to 24 L/seg, condensation has decreased but the generator stator temperatures have increased in 4°C (from 84 to 88°C).
Are there some problem to operate the generator with 4°C more?
Thanks, bye there!