Geby
Mechanical
- Sep 12, 2005
- 6
I am attempting to solve a pump cavitation problem in a condenser water system with an open cooling tower. The pumps are base mounted single suction with inlet strainers installed. I am thinking that the additional pressure drop caused by the inlet strainers may be causing the pumps to cavitate, but have not tested the theory yet. I wanted to throw out this general question to the audience: Since cooling towers are normally equipped with sump strainers, is it really necessary to keep the pump inlet strainers installed beyond initial startup? Yes, some minor junk like pine needles will get past the sump strainer and into the water loop, but I do not think that this kind of thing would cause any major pumping problems, and we do have a solids seperator in the loop. I am thinking that pump inlet strainers installed in an on an open condenser water system could easily reduce the available NPSH below that required.