Support cooling tower from piers in the sump located to contact the cooling tower support points. Waterproof the sump walls. Provide deeper section to locate intake & screen. Design of intake is critical. refer to Cameron Hydraulic Data section on Intake design. It is on page 1-22 to 1-26 on the 16th Edition. Anchor pumps adequately and fill sump before starting pumps. Jog them first as a precaution. Provide galvanized sheetmetal skirt around cooling tower side and outer edge of sump to cover gap. Provide low level shutoff, low sump level alarm, high sump level alarm, cooling tower vibration limit switch, freeze protection heater; low sump temperature alarm, coling tower bypass control.Provide plastic grating on service walkways. Require access doors in cooling tower; access ladder; handrail; light; lightning protector; disconnect switches.