MCMortley:
What you have described is a conventional, mechanical refrigeration system driven by a centrifugal compressor. As such, you incorrectly call it “a water cooled centrifugal compressor chiller” when, in reality, it is the refrigerant condenser that is water cooled. The condenser, besides the compressor, is one of the main components in the refrigeration cycle that you are describing and its production of condensed refrigerant is what is the key element producing “cold” downstream in an evaporator that is presumably producing a “chilled” process fluid.
You have asserted various statements which I list and comment on:
1) “Increasing the condenser water temperature range reduces the condenser water flow, which requires smaller pumps and piping.” You are basically correct if you are maintaining the initial cooling water temperature entering the condenser constant year-round. If you are using a cooling tower to produce the cooling water (CW) temperature, I doubt you can maintain the product CW supply (CWS) temperature constant year-round, but I will assume that the variance is negligible.
2) “It also increases the required condenser pressure while improving the LMTD for the cooling tower.” Here is where you loose me and, I believe, you’ve lost your logic. By increasing the CW temperature range (with a constant inlet temperature) you can only mean that the return CW temperature is as high as you (actually, the CW tower) can accept it. Normally, this cooling water return (CWR) is maintained at a maximum of 120 oF on a practical basis. This is the maximum limit on most CW tower systems. If you increase the condenser water temperature range you can only mean that you are lowering the CWS temperature. With a properly designed and applied condenser, you can expect to achieve a 5 oF approach to the CWS temperature. This means that with an 80 oF CWS, you can expect an 85 oF refrigerant condensed product. We engineers know our Thermo and, consequently, we know that the condensed refrigerant product is a saturated fluid whose vapor pressure is directly related to its temperature. The lower the temperature, the lower the vapor pressure. The same vapor pressure is the system pressure in the condenser and receiver, prior to going to the refrigeration expansion valve and the downstream evaporator. Consequently, you are wrong in stating that the condenser pressure increases with an increased temperature range. Rather, the condenser pressure will decrease when you have a ceiling on the CWR and you increase the temperature range - because this means that the CWS temperature has to be lower. Additionally, there is NO LMTD involved in the design and operation of a cooling water tower. The Log Mean Temperature Difference (LMTD) is a pseudo-driving force derived for use in describing the overall temperature driving force in the Fourier equation as applied to the design of tubular heat exchangers – not simultaneous heat and mass transfer unit operations such as a cooling tower. Sorry, but I’m quoting basic engineering knowledge to your statement.
3) “Increasing the condensing pressure on the chiller will result in a combination of increased chiller cost and reduced performance.” Not necessarily true, but you fail to state that you are implying capital costs rather than operating costs. You also fail to identify the expected performance you foresee as “reduced”. An increased condenser pressure for most refrigerants identifies a lower Latent Heat of Vaporization (or, in your case, condensation). Consequently, you will require less water flow rate. The Latent Heat requirement is easily seen in the Mollier Diagrams for refrigerants as found in ASHRAE publication: “Thermodynamic Properties of Refrigerants” (ISBN 0-910110-47-6). The “Tit” formed by most refrigerants in the Mollier Diagram is more slender as the pressure increases – until the Critical Point is reached.
Now to address your specific question: “how does reduced condenser water flow rate cause the required condenser pressure to increase in the chiller?” Answer: If you reduce CWS to a refrigerant condenser, you will condense less refrigerant (rate wise) and your CWR temperature will increase. You will still be condensing, but at a lower rate and at a higher temperature. This will yield a higher operating pressure within the condenser and the receiver and, if the process persists, will cause an over-pressure situation on the condenser and receiver, activating their pressure safety relief valves. You must supply the correct and necessary rate of CWS to the condenser at all times while the unit is operating in order to condense all the refrigerant entering at a specified rate. The more CWS you can furnish and the colder that same CWS, the faster the refrigerant vapors will condense and the colder and the lower the vapor pressure inside the condenser-receiver assembly. The colder the refrigerant liquid in the receiver, the better and more efficient the chiller operation. That is my personal design and operational experience with Ammonia, CO2, Freons, and other refrigerants in industrial applications.
Summarizing: I don’t know where you gathered or got your assertions on the mechanical refrigeration cycle, but I would recommend you do some boning up on the basic and detailed engineering theory of mechanical refrigeration as found in good text books such as the ASHRAE Fundamentals Handbook or Ernest Ludwig’s classic “Applied Process Design for Chemical and Petrochemical Plants”, Volume 3.
I hope I’ve been of some help in orienting you on refrigeration thermodynamics.
(As an aside, how does your basic query rate a "Star"?)
Art Montemayor
Spring, TX