michael333
Mechanical
- Jun 15, 2007
- 20
Hello,
I have (3) P-K condensing boilers (MACH Model C-300 w/ ENVI Control) for a small job. Each C-300 is rated as follows:
Output 276,000 BTU/hr heating capactiy at full-fire
Flow rate @ 20 delta T: 28 GPM
Flow rate @ 40 delta T: 14 GPM
Each C-300 has its own isolation valve associated with it.
I stated in my sequences for each boiler to control its own isolation valve to OPEN/ClOSE based on operation. B-1 is master, the other 2 boilers are the slaves.
Stated in my sequences 140 deg F maintained to the system, 120 deg F returning.
2-way control valves at all 30 boxes, 4 FCUs, and 2 AHUs with recovery wheels.
Also, have a bypass valve out in the HW system.
Total peak heating load for facility: approx 650,000 BTU/hr
Had 2 inline pumps, operating in parallel, providing approx 68 GPM @ 41 Hz to the heating system at full-flow according to a submitted TAB report.
When I was onsite 2 weeks ago, I observed all 3 boilers ON to maintain setpoint of 140 deg F and modulating their isolation valves accordingly. It was 55 - 60 deg F outside. I would've thought that only 1 boiler would be operating to maintain the 140 setpoint, not 3 of them. Also, noticed 46 Hz for each of the inline pump VFDs operating in parallel.
Contractor is telling me that the lead master boiler B-1 is tripping out on high-fire when its associated isolation valve opens up for flow to the boiler. Tells me its a design issue.
Can anyone speak to this? Has anyone ever ran across this issue before with a similar design? Any advise or input would be appreciated.
Thanks,
I have (3) P-K condensing boilers (MACH Model C-300 w/ ENVI Control) for a small job. Each C-300 is rated as follows:
Output 276,000 BTU/hr heating capactiy at full-fire
Flow rate @ 20 delta T: 28 GPM
Flow rate @ 40 delta T: 14 GPM
Each C-300 has its own isolation valve associated with it.
I stated in my sequences for each boiler to control its own isolation valve to OPEN/ClOSE based on operation. B-1 is master, the other 2 boilers are the slaves.
Stated in my sequences 140 deg F maintained to the system, 120 deg F returning.
2-way control valves at all 30 boxes, 4 FCUs, and 2 AHUs with recovery wheels.
Also, have a bypass valve out in the HW system.
Total peak heating load for facility: approx 650,000 BTU/hr
Had 2 inline pumps, operating in parallel, providing approx 68 GPM @ 41 Hz to the heating system at full-flow according to a submitted TAB report.
When I was onsite 2 weeks ago, I observed all 3 boilers ON to maintain setpoint of 140 deg F and modulating their isolation valves accordingly. It was 55 - 60 deg F outside. I would've thought that only 1 boiler would be operating to maintain the 140 setpoint, not 3 of them. Also, noticed 46 Hz for each of the inline pump VFDs operating in parallel.
Contractor is telling me that the lead master boiler B-1 is tripping out on high-fire when its associated isolation valve opens up for flow to the boiler. Tells me its a design issue.
Can anyone speak to this? Has anyone ever ran across this issue before with a similar design? Any advise or input would be appreciated.
Thanks,