Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Conduit Cast into Composite Slabs 1

Status
Not open for further replies.

NashEng

Structural
Jul 1, 2005
1
The contractor would like to cast electrical conduit into the ribs of a composite slab. The UL assembly rating technically doesn't provide an allowance for it, and if the conduit projects up past the ribs it will reduce the effective area of concrete.

Does anyone have any references on this subject, what is allowable and what isn't?

What is the state of the practice? Are you allowing it on your jobs?
 
Replies continue below

Recommended for you

Some small, minimal conduit can be put in the slab as long as:

it does not affect the composite action of the beams or slab

it does not displace the reinforcing

it is not so closely spaced that it creates a weak spot.

it does not affect the fire rating

sufficient cover is provided top & bottom

In general, the placement of conduit or pipes shall comply with ACI 318, section 6.3.

For thin slabs, it is often not possible to have conduit crossing over each other.

It is your call.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor