Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Conduit filling as per BS/IEC

Status
Not open for further replies.

tlp23

Electrical
May 15, 2011
7
Dear All,

Could you please let me know the percentage cable filling allowed for a conduit as per BS/IEC.

Regards,
Lakshmipati
 
Replies continue below

Recommended for you

I'm not familiar with BS standards, but the NEC limits conduit fill to 40% for three or more conductors. (e.g. Art 344.22 for rigid conduit)

 
Dear all,

Thanks for the answers.

7another4,

could you please let me know the section in which it is given as 40% filling.

Regards,
Lakshmipati
 
I think it is in The On-Site Guide .I took this sentence from a flexible conduit manufacturer:
"UK wiring regulations BS7671, recommend that the total cross sectional area of the sum of the individual cables should not exceed 40% of the cross sectional area of the conduit"
And other stated:
"BS7671-2008 provide tables for cable and conduit factors, these can be found in the current IEE On Site guide BS7671-2008 Appendix 5 Pages 117 to 120"
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor