Conduit Size for grounding electrode conductor

Status
Not open for further replies.

naderalfeki

Electrical
Nov 6, 2017
1
In case the grounding electrode conductor will be installed in embedded conduit, is there any limitation on the filling ratio of the conduit?
knowing that the conductor within the conduit will be drawn and installed before casting concrete.
 
Replies continue below

Recommended for you

I hope that this is non-ferrous conduit.
The Canadian Electrical Code states that the overall area of the conductor may not exceed 53% of the internal area of the conduit.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
The conduit fill requirements still apply. Like Waross said make sure using non-ferrous conduit or cut slits in where the conduit enters the enclosure, etc.
 