Conduits in slabs

Status
Not open for further replies.

slickdeals

Structural
Apr 8, 2006
2,261
0
36
US
I am hoping someone can enlighten me on why ACI 318-14 and onwards, the requirements for conduit spacing (3 * diameter) and conduit diameter (less than 1/3 slab thickness) have been removed and replaced with a generic language. Refer to ACI 318-14 Sections 20.7 and 26.8.
 
Replies continue below

Recommended for you

Without having the code in front of me, I’d guess they left it out because it might be in ACI 301, the specification. Some of the mix design requirement are only in ACI 301 where they were in both prior to ACI 318-14
 