Nandit

Computer
Dec 28, 2013
1
0
0
AU
Hi , I am trying to operate GS1-21P0 using RS-485 serial port in P3-550. I am using modbus RTU protocal to communicate. However, my GS1-21P0 is showing an error code cE01.
Can any one help on this.

 
Replies continue below

Recommended for you

To clear up any confusion, they are a VFD and PAC from AutomationDirect, respectively.

RTFM. It says:
GS1 Manual said:
Communications Warning:
Illegal command code - The
command code received in the
command message is not
available for the AC drive.

In other words, you're sending a command from the PAC that the drive does not recognize. Rewrite the command you're sending so it is valid for the drive.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.