From NFPA 14 "Standard for the Installation of Standpipe, Private Hydrant, and Hose Systems" 2000 Editio
Section 5-9.1 requires the system designed for 500 gpm at the most remote standpipe:
5-9.1 Class I and Class III Systems.
5-9.1.1* Minimum Flow Rate.
For Class I and Class III systems, the minimum flow rate for the hydraulically most remote standpipe shall be 500 gpm (1893 L/min). The minimum flow rate for additional standpipes shall be 250 gpm (946 L/min) per standpipe, with the total not to exceed 1250 gpm (4731 L/min).
But right below it the calculation procedures call for each standpipe to be designed for 250 gpm.
5-9.1.2* Hydraulic Calculation Procedure.
Hydraulic calculations and pipe sizes for each standpipe shall be based on providing 250 gpm (946 L/min) at the two hydraulically most remote hose connections on the standpipe and at the topmost outlet of each of the other standpipes at the minimum residual pressure required by Section 5-7. Common supply piping shall be calculated and sized to provide the required flow rate for all standpipes connected to such supply piping, with the total not to exceed 1250 gpm (4731 L/min).
Seems to me if you design each standpipe at 250 gpm, per 5-9.1.2, you will never get the system to pass acceptance test which requires 500 gpm be flowing from the top outlet.
In the past I've always calcualted each standpipe to deliver 500 gpm wich 250 from each additional standpipe and I will continue to do so. The problem is I am helping a friend pass NICET for testing.
Section 5-9.1 requires the system designed for 500 gpm at the most remote standpipe:
5-9.1 Class I and Class III Systems.
5-9.1.1* Minimum Flow Rate.
For Class I and Class III systems, the minimum flow rate for the hydraulically most remote standpipe shall be 500 gpm (1893 L/min). The minimum flow rate for additional standpipes shall be 250 gpm (946 L/min) per standpipe, with the total not to exceed 1250 gpm (4731 L/min).
But right below it the calculation procedures call for each standpipe to be designed for 250 gpm.
5-9.1.2* Hydraulic Calculation Procedure.
Hydraulic calculations and pipe sizes for each standpipe shall be based on providing 250 gpm (946 L/min) at the two hydraulically most remote hose connections on the standpipe and at the topmost outlet of each of the other standpipes at the minimum residual pressure required by Section 5-7. Common supply piping shall be calculated and sized to provide the required flow rate for all standpipes connected to such supply piping, with the total not to exceed 1250 gpm (4731 L/min).
Seems to me if you design each standpipe at 250 gpm, per 5-9.1.2, you will never get the system to pass acceptance test which requires 500 gpm be flowing from the top outlet.
In the past I've always calcualted each standpipe to deliver 500 gpm wich 250 from each additional standpipe and I will continue to do so. The problem is I am helping a friend pass NICET for testing.